 Post subject: Cat 0 or Cat 2 PPE
PostPosted: Sat Nov 05, 2011 6:15 pm 
Offline

Joined: Thu Jun 02, 2011 4:47 am
Posts: 3
Hi, Im from Austrialia,
We are currently using the US standards for our sites.

We have perfromed some sample sites. One issue I have is that a lot of the sites Distribtuion boards etc are Cat 0.
When we follow the table (in luie of an arc flash study) in NFPA it states that Cat 1- 2 is required for exposure to live part.

Should we advise our clients electrcial workers to use min Cat 2 for electrcial work regardless if it is a cat 0 switchboard?

Thanks for any advice, I have been following the fourm but until now havent asked any questions.
Thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Nov 06, 2011 1:33 pm 
Offline

Joined: Fri Sep 05, 2008 8:10 am
Posts: 36
If the equipment is determined through the Incident Energy Analysis to meet the requirements to allow for CAT 0 PPE then that is that, no using the tables. If you are using the tables, which you stated are in lieu of the analysis, how have you determined the equipment ot be CAT 0?

I have heard of some sites using a canned scenario to determine, for example, given a short circuit finding the distance where the incident energy is increased. They then apply this scenario to other equipment instead of performing a specific study for each site.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Nov 10, 2011 1:39 am 
Offline

Joined: Thu Jun 02, 2011 4:47 am
Posts: 3
We advised the client on typical worst case and released a table based on the sample site we did.
We are now performing detailed studies on each site.
When equipment is calculated to be cat0 , we still label cat 2 for electrical work on that equipment. We are concerned with the reliability of the switch gear and possible changes in fault levels, we are recommending that min ppe for electrical work ( testing , fault finding) is cat2. I did argue this with the head Engeneer and his view was better to be cat2 if an arc occurs than cat0. Do you think that is ok .


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Nov 10, 2011 7:32 am 
Offline
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 411
Location: Spartanburg, South Carolina
It is certainly OK to use a higher category PPE than the calculations indicate. Annex H of NFPA 70E describes a simplified two-category approach that could be used. You might also consider modified Cat 2 PPE (for example 8 cal/cm┬▓ rating but without the balaclava) for incident energies below 4 cal/cm┬▓.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883