 Post subject: Rubber Insulating Gloves, Testing/Issuing
PostPosted: Tue Apr 10, 2012 6:00 pm 
Offline

Joined: Thu Jan 07, 2010 6:42 am
Posts: 35
Location: Bowling Green, KY
I was recently issued "new" gloves that are dated July 2010. I raised the issue of them being in an expired state and that they should have been tested again proir to them being issued. I cited NFPA70E Table 130.7(C)(6)(c) as my reference for my opinion. At the bottom of the table it states "If the insulating equipment has been electrically tested but not issued for service, it may notbe placed into service unless it had been electrically tested within the previous 12 months."
I was told that they could issue them as NFPA70E 250.2(B) says they they can issue them as long as it hadn't exceeded 3 years. I noticed that it also says "Unless specified otherwise by the respective ASTM Standards."
Would this be ASTM F 496? I see it referenced but I don't have access to ASTM Standards.
I also saw (from another post) OSHA 1910.137 Table I-6 which appears to echo NFPA70E Table 130.7(C)(6)(c).
I could sure use some help from someone here, I think I'm right, but I'm no expert.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Apr 11, 2012 8:14 pm 
Offline
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 1878
Location: North Carolina
Irrespective of the standards, this is an OSHA regulatory requirement: OSHA 1910.137(b)(2)(xii). OSHA doesn't even mention the "3 year rule" in NFPA 70E. You can access OSHA 1910.137 which covers insulated gloves extensively right on their web site for free. [url="http://www.osha.gov"]www.osha.gov[/url] and go to "regulations".

Glove testing is covered ASTM D 120-09. F 496 is for in service testing...roll tests or inflation tests.
"If the insulating equipment has been electrically tested but not issued for service, it is not permitted to be placed into service unless it has been electrically tested within the previous 12 months."


That section is totally misquoted. The exact quote is ""...but in no case shall the interval exceed 3 years, unless specified otherwise by the respective ASTM standards." So in other words, the paragraph is a catchall for anything that doesn't have a specific ASTM standard. Gloves do not count in that list.

Answer: OSHA says 12 months. ASTM says 12 months. NFPA 70E says 12 months. Looks pretty cut and dry to me.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Apr 14, 2012 4:30 pm 
Offline

Joined: Thu Jan 07, 2010 6:42 am
Posts: 35
Location: Bowling Green, KY
Thank you sir! I figured I was right but was just needing verification.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Apr 16, 2012 8:24 am 
Offline

Joined: Mon Nov 19, 2007 5:25 am
Posts: 29
Location: Titusville, Fl.
Since, ChevsMark does not have a copy of the ASTM 496, the following lists the entire electrical test section for insulating gloves:
7. Electrical Test

7.1 Electrically retest gloves or sleeves issued for service.

Base the interval between date of issue and retests on work

practices and test experience. It shall not exceed 6 months for

gloves and twelve months for sleeves. Gloves or sleeves that

have been electrically tested but not issued for service shall not

be placed into service unless they have been electrically tested

within the previous twelve months.

Bear inmind although the test period is 12 months, the electrical worker can only use the gloves for 6 months therein....


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883