Hi ....someone can help me?

If I had a equipment with 11cal/cm2 as a result of an arc flash study, can i use a 12cal/cm2 arc flash suit and comply NFPA 70E ? or i have to use a 25 arc flash suit?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Apr 17, 2013 5:09 pm 
Offline

Joined: Wed Jan 26, 2011 12:04 pm
Posts: 32
mauricioville wrote:
Hi ....someone can help me?

If I had a equipment with 11cal/cm2 as a result of an arc flash study, can i use a 12cal/cm2 arc flash suit and comply NFPA 70E ? or i have to use a 25 arc flash suit?

I might be missing something but, yes, you can use a 12 cal suit (with a number of other provisos that must accompany the PPE alone).


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Apr 20, 2013 5:17 am 
Offline
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 711
Location: Rutland, VT
As long as the PPE is rated for >11cal/cm^2, yes. This would include all the PPE including baclava, face shield, etc.

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Apr 21, 2013 2:10 pm 
Offline
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 445
Location: Wisconsin
See 70E Annex H for some guidance.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Apr 22, 2013 8:04 am 
Offline
Sparks Level

Joined: Wed Oct 29, 2008 6:06 am
Posts: 136
Location: Michigan
Quote:
If I had a equipment with 11cal/cm2 as a result of an arc flash study, can i use a 12cal/cm2 arc flash suit and comply NFPA 70E ? or i have to use a 25 arc flash suit?


Yes, if you're at the working distance at which the incident energy was calculated you would meet 70E requirements.

However, your company's Electrical Safety Procedure determines which form of PPE information is included on the arc flash label (1. incident energy, 2. minimum arc rating of clothing, 3. highest required PPE level or 4. highest HRC) and how that information should be interpreted by the employee.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Apr 22, 2013 12:33 pm 
Offline
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 411
Location: Spartanburg, South Carolina
Further to what A King says - if the company has standardized on certain levels of PPE, and puts level 3, or 25 cal/cm┬▓ on the label, then you need to use 25 cal/cm┬▓ rated PPE.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Apr 29, 2013 7:10 am 
Offline
Sparks Level
User avatar

Joined: Sun Jan 04, 2009 5:00 pm
Posts: 265
Location: Louisville, KY
This is why you do an arc flash study. You may also wish to do a risk analysis to look closer at the actual task. If it is performed at a greater distance than the calculated "working distance" you might be able to reduce the PPE level. I never recommend doing any task with risk of ignition in flammable clothing. Just use something with the arc rating you will be exposed to. jGhrist points out something important also. Never put something on the labels you are not required or are not going to do. Having 12 cal and HRC3 is never recommended and a misunderstanding of NFPA 70E that was perpetuated by IEEE 1584-2002. It will be corrected in the next version and most software companies have in corrected now. HRC's and calculations don't mix. See Annex H.3 in NFPA 70E 2012


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Apr 29, 2013 8:18 am 
Offline

Joined: Mon Jan 31, 2011 2:53 pm
Posts: 12
Thanks for all of you !!


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 8 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883