waleed030 wrote:
For 120 V I am not aware of any published data showing arcs exceeding 1.2 cal/cm^2 but there are a few OSHA investigations where hospitalization occurred on the hands due to close proximity to an arc. 208 V 3 phase has more research and sustainable arcs do exist, and OSHA investigated a single case in 2009 involving a fatality with a 240/120 construction panel. Right now IEEE 1584 gives guidance of less than 1.2 cal if fed by a single transformer rated 208 V or less, and 125 kVA or less. NESC gives guidance of 4 cal for everything under 300 Volts because this is the lowest rating accepted in the utility industry. So the short story is generally everything is under 1.2 cal but pay attention to transformer sizes. If they are large, I would roll up to the NESC recommendation of 4 cal.