When selecting an 8 cal or 12 cal arc flash kit.
Is the balaclava required as to the standards or is the addition of it just for more personal choice providing more protection?




Terry


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Balacalva Requirement
PostPosted: Thu Mar 24, 2016 9:26 am 
Sparks Level
User avatar

Joined: Tue Nov 12, 2013 6:31 am
Posts: 238
Location: Port Huron, Michigan
A balaclava is required by 70E. Table method requires it over 4 cal, calculation method would require it over 1.2 cal.

I would select a 12 cal in that case, so as not to limit yourself to only 8 cal with your equipment.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Balacalva Requirement
PostPosted: Thu Mar 24, 2016 9:32 am 

Joined: Fri Sep 19, 2008 4:45 pm
Posts: 27
Location: Canada
Thank you

So a kit that is provided "without" the balaclava is not in compliance unless the end user has their own balaclava on hand.
Is that correct?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Balacalva Requirement
PostPosted: Thu Mar 24, 2016 9:40 am 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2178
Location: North Carolina
There is an additional wrinkle to this. OSHA 1910.269 for outdoor overhead equipment recommends balaclava is not required until 9 cal/cm2 or higher.

There is a TIA that corrects the discrepancy in annex H as far as 1.2-4 cal/cm2 goes.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Balacalva Requirement
PostPosted: Thu Mar 24, 2016 9:46 am 

Joined: Fri Sep 19, 2008 4:45 pm
Posts: 27
Location: Canada
So it looks like there might be grey area in the regs there.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Balacalva Requirement
PostPosted: Thu Mar 24, 2016 11:14 am 
Sparks Level
User avatar

Joined: Tue Nov 12, 2013 6:31 am
Posts: 238
Location: Port Huron, Michigan
If you are following 70E you should be using a balaclava for anything greater than 1.2 cal/cm2. If you are not following 70E, as Paul mentioned, you can leave the balaclava out until you get to 9 cal.

If there is a chance that an arc flash could occur when the worker is not perfectly square to the flash, then a balaclava should be used. Wouldn't really want to take something greater than 1.2 cal to the back of the head with no protection.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Balacalva Requirement
PostPosted: Thu Mar 24, 2016 1:22 pm 

Joined: Fri Sep 19, 2008 4:45 pm
Posts: 27
Location: Canada
Okay thank you for the clarification on this.

Much appreciated.



Terry


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 7 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883