Hello!
Does anyone have any knowledge of EN166 for rating of face protection. I read that one helmet with integrated visor was rated 12kA/1s 380-400V. What actually does this mean is this numbers possible to convert to cal/cm2 or is this completely something else?

Super happy for any answer :)


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: EN166 for rating of face protection
PostPosted: Wed Dec 06, 2017 6:45 am 

Joined: Wed Nov 01, 2017 6:09 am
Posts: 32
No answers here?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: EN166 for rating of face protection
PostPosted: Wed Dec 06, 2017 10:50 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
There is not way to convert to cal/cm2 from the voltage and current ratings as there are many other factors. The protection must be tested. Presently IEC TC 78 (I am Chair of the Committee that is responsible for this standard as well as around 40 others) has a Project Team that has been developing what will be 62819 Ed.1.0: Live working - Eye, face and head protectors against the effects of electric arc - Test methods and requirements. It is in the early stages but will eventually provide an international test method.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883