Was hoping to get some input on some IE calcs I have for quite a few pump jack sites out here in TX. 12,470 dist to low kVA step down banks between 30-45. T style cutouts clear fault in about a cycle so I end up with IE of .07-.09 cal/ cm^2. Anyone have any thoughts on necessary PPE for this instance? Guys already have leather gloves, arc rated clothing, hearing protection, safety glasses, and hardhats; however, I'm, wondering if adding a face shield might not be a bad idea...Any thoughts? Would this be unnecessary/ over kill?

Thanks!!

_________________
Under qualified but over confident


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: PPE for VERY Low IE
PostPosted: Tue Jan 16, 2018 7:43 pm 
Offline
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 1880
Location: North Carolina
I think IEEE 1584 states that results below 0.1 cal/cm2 are invalid.

Human skin is good for 1.2 cal/cm2. That's why NFPA 70E-2015 and later has a lower cutoff of 1.2 cal/cm2 for the PPE. Previous editions recommended avoiding meltable fiber clothing (and NESC still does) due to a possibility of secondary injuries from having melted synthetic fiber glued into the skin and exacerbating a burn but that's about it. Up until the point that it melts, the stuff has a pretty decent arc rating even if it's not rated.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: PPE for VERY Low IE
PostPosted: Mon Jan 22, 2018 9:37 am 
Offline
Sparks Level

Joined: Fri Apr 15, 2011 7:43 am
Posts: 164
Location: Colorado
When Paul says "Human skin is good for 1.2 cal/cm2" he means we can fully recover from a burn at that energy. It is slightly more than holding your hand over a disposable lighter


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: PPE for VERY Low IE
PostPosted: Tue Jan 23, 2018 3:15 pm 
Offline
Sparks Level
User avatar

Joined: Sun Jan 04, 2009 5:00 pm
Posts: 265
Location: Louisville, KY
1.2 is a second degree burn.

I recommend looking at the work situation and do a risk assessment.

Some companies use arc rated, cut resistant sleeves and AR gloves and allow a cotton t-shirt.

There are a few manufacturers of the sleeves and gloves.

If there is a shock hazard, of course, rubber gloves with protectors is required.

Hugh Hoagland


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: PPE for VERY Low IE
PostPosted: Mon Jan 29, 2018 2:31 pm 
Offline
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 411
Location: Spartanburg, South Carolina
You will find that the IE on the low side is much, much higher.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883