It is currently Wed Nov 11, 2026 10:34 am



Post new topic Reply to topic
Author Message
 Post subject: Faceshield use with back to hazard
PostPosted: Mon Apr 09, 2018 7:55 am 

Joined: Tue Nov 21, 2017 9:09 am
Posts: 2
I have an area that requires CAT 2 PPE bases on incident energies. Workers will be operating a 4KV breaker from a remote station. Because of design the remote station is only 2m away from breaker, therefore requiring CAT 2 based on our plant conditions. Remote station will cause worker to have his/her back to the breaker. Will the faceshield cause a "scoping" of plasma should an arc-flash occur? I can not find any information in z462-18 talking about body position with use of a faceshield. I am likely to recommend use of a hood to play it safe but would love and information if anyone has it.
FYI, faceshield use would be with a balaclava.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 1 post ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883