Thank you for the thoughtful reply! I am referring to 220 volt (230 volt) low voltage single phase circuits - derived from say a 380/220V three phase 4 wire system.
In that regard did you mean to say
three phase results below:
Quote:
If the former then there has been testing done on single phase vs. 3 phase arcs and frankly there isn't a huge difference between them in terms of the result (incident energy) so IEEE 1584 both in the current (2002) edition and the upcoming draft edition state to just use single phase results for conservative purposes for calculating incident energy.
Thanks again
Bill