It is currently Wed Sep 30, 2026 1:05 am



Post new topic Reply to topic
Author Message
 Post subject: EPP Arc Flash expiration?
PostPosted: Fri Mar 06, 2020 9:45 am 

Joined: Fri Dec 30, 2016 3:13 pm
Posts: 6
Excuseme my english is not perfect.

What is the lifespan of a arc flash suit?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: EPP Arc Flash expiration?
PostPosted: Mon Mar 09, 2020 12:47 pm 
Sparks Level

Joined: Sat Nov 21, 2009 10:23 pm
Posts: 124
Location: Ohio
If the arc rated PPE is kept clean, it will depend on the number of and type of launderings. As a general rule of thumb, a large percentage of PPE manufacturers put a limit on the number of launderings to 60-80. I am limiting my comment to Category #2 PPE. Category #4 will vary, in that case, consult the mfg.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: EPP Arc Flash expiration?
PostPosted: Mon Mar 16, 2020 9:03 am 
Sparks Level
User avatar

Joined: Sun Jan 04, 2009 5:00 pm
Posts: 288
Location: Louisville, KY
There is no standard requirement on replacement of Arc Flash Suits. ASTM F18 is working on a standard and it could include recommendations on replacement.

The best advice we have seen to date is following the manufacturer's recommendations.

Face shield manufacturers typically indicate that they should be replaced when the shield becomes scarred or in about 2-5 years depending on how they are stored and cared for.
Hard hat suspensions are to be replaced every year and the hard hat 2-5 years depending on the manufacturer's recommendations.

Fire fighter's turnout gear gets replaced every 10 years but it is exposed to fire on a regular basis. We have tested used arc flash suits and not seen failures. The washing frequency is VERY low (if they are washed at all) in most plants.

We recommend washing periodically to remove any flammable contaminants but done hood designs make washing difficult.

The 10 year rule is reasonable but many will last much longer than that.

Hugh Hoagland
ArcWear/e-Hazard


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883