 Post subject: What level of ARC PPE would be required at motor terminals?
PostPosted: Tue Mar 17, 2020 8:59 am 
User avatar

Joined: Mon Feb 03, 2020 3:55 am
Posts: 1
Location: South Africa
Hi
I am new to this forum and to the Arc flash and live work regulations. We are reviewing our company's procedures for this and I have found this forum very helpful.

I would like to find out what the ARC flash PPE recommendations would be for live testing on either the field isolator or motor terminals of a motor in the field. Our MCC's are mostly 525V AC and have fault levels below 15kA, they are equipped with Isolators, fuses, contactors and overload units. I would think that it would not be more that HRC 1 or perhaps even 0 seeing that the fuses should bring the fault levels down significantly along with the length of cable from the MCC to the motor (probably between 20 and 50m). We would not want to be doing the ARC calculations for each and every motor if it is not needed.

Your input would be greatly appreciated.

_________________
Regards
G Human


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: What level of ARC PPE would be required at motor termina
PostPosted: Thu Mar 19, 2020 6:04 am 

Joined: Mon Aug 04, 2014 5:19 pm
Posts: 19
The arc fault energy is likely low but unless calculated not known.

This is similar to the dilemma of labeling Horsepower Rated disconnects and the amount of work needed to do all those calculations.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: What level of ARC PPE would be required at motor termina
PostPosted: Sat Mar 21, 2020 10:49 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
Jackero wrote:
Hi
I am new to this forum and to the Arc flash and live work regulations. We are reviewing our company's procedures for this and I have found this forum very helpful.


Welcome to the Arc Flash Forum! Adding to Jimmy's comment, it is really hard to tell since the incident energy is a function of BOTH the fault current AND the device clearing time. The clearing time is often the big question but if your device trips in a few cycles, the energy is likely lower (just a thought, not a formal opinion or conclusion)


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: What level of ARC PPE would be required at motor termina
PostPosted: Mon Mar 23, 2020 6:12 pm 

Joined: Sun Feb 14, 2010 9:28 pm
Posts: 21
Location: Queensland
As a first step in mitigating the risks of arc flash, you should consider why you need to perform this task live, rather than isolate, connect test equipment and de-isolate.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883