In reference to 70E, am I correct to assume that the insulating gloves are not required for simple Arc-Flash PPE, but only when crossing the Prohibited Approach Boundary?

Conversely, when the insulating gloves are coverered in leather protectors, that they are an acceptable part of the Arc-Flash PPE?

What do the Class ratings of rubber insulating gloves signify? Are they simply voltage ratings?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Oct 24, 2009 11:55 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
Volta wrote:
In reference to 70E, am I correct to assume that the insulating gloves are not required for simple Arc-Flash PPE, but only when crossing the Prohibited Approach Boundary?


No, when crossing the RAB

Volta wrote:
Conversely, when the insulating gloves are coverered in leather protectors, that they are an acceptable part of the Arc-Flash PPE?
Yep

Volta wrote:
What do the Class ratings of rubber insulating gloves signify? Are they simply voltage ratings?


Yep, the class is the max use voltage, the type is the material they are made of.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883