PostPosted: Sat May 29, 2010 2:23 am 
Offline

Joined: Sun Nov 16, 2008 12:01 pm
Posts: 44
Will it change the hrc level of the switch or eqiupment if a remote control device is used to do the task ?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat May 29, 2010 7:10 am 
Offline
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
PUCKMAN wrote:
Will it change the hrc level of the switch or eqiupment if a remote control device is used to do the task ?


It changes nothing at the equipment but if the person operating the equipment can do it remotely from outside the arc flash boundary no PPE would be required.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Jun 03, 2010 4:32 pm 
Offline
Sparks Level

Joined: Sun Sep 23, 2007 5:00 pm
Posts: 108
Location: Calgary, Alberta, Canada
I have to agree with haze10 original post. We have to use risk assessment related to our operation or maintenance work on energized electrical equipment. We have to apply control measures from a practical and appropriate perspective. We also want workers NOT to fear energized electrical equipment, rather respect it. We need to also apply the concept of normal and abnormal conditions to energized electrical equipment. Abnormal conditions cause arc flash and shock.

With the door closed and equipment operating normal, no arc flash or shock PPE is required to open and close a circuit breaker or disconnect swiitch with a written procedure and training on the procedure.

There is a low risk under normal conditions that opening and closing a circuit breaker and switch would arc flash. The equipment is manufacturered to a Standard, rated for this transistion many time under no load, and desiged to operate.

The worker needs to assess if normal conditions exist when the operate it.

If you want a worker to wear arc flash gear to do this, then are you implying you want them to wear it to read a panel meter.

Just because we have an arc flash label on equipment doesn't mean there is an arc flash risk, it is task depedendant and based on risk which increase with aging, lack of maintenance, contamination due to operating environment, etc..

Regards;
Terry Becker, P.Eng.
ESPS Electrical Safety Program Solutions INC.
terry.becker@espsi.ca
403-465-3777


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 23 posts ]  Go to page Previous  1, 2

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883