Hi

NFPA 70E 130.7(C)(13)b) clearly says that a face shield without arc rating shall not be used. Now, when you buy one, the ATPV is clearly written on the face shield side.

I thought it was the same for coveralls but I can't find where it's written, if it is... Was it in NFPA 70E 2004?

So, is it a problem if someone buy a 8.2 cal/cm2 FR coverall and if this ATPV is not written on the coverall label?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Jan 27, 2010 1:35 pm 
Offline
Sparks Level

Joined: Tue Feb 24, 2009 7:05 am
Posts: 252
ASTM F 1506 says that a garment can meet ASTM F 1506 only if the label publishes an APTV or EBT value, and the label must say that the garment meets ASTM F 1506.

NFPA 70E says that to be considered arc rated, a garment must meet ASTM F 1506.

Hugh can probably tell you more about this.

Who's the manufacturer of the coverall?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Jan 27, 2010 2:32 pm 
Offline
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1245
Location: Scottsdale, Arizona
ASTM F1506 DOES require the arc rating on the label.

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Feb 12, 2010 2:02 pm 
Offline

Joined: Tue Jul 21, 2009 8:59 am
Posts: 7
Location: Tennessee
Coverall

Buyer beware, there a number of products coming in from foriegn countries that claim to be FR and Arc rated. If they don't meet the 1506 standard then stear clear to protect yourself.

Garments must meet the following requirements under ASTM F1506:

*Components of the garment must be flame resistant.
*Metal components can not be exposed to the wearer.
*Labels requiring the manufactures name, cut number and date of manufacturing.
*Labels must state the garment meets ASTM F1506.
*Labels must indicate the Arc Rating of the garment either as a single layer or combination.
*FR Thread must be used in the construction of the garment.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Apr 21, 2010 6:03 pm 
Offline

Joined: Thu Nov 20, 2008 3:00 pm
Posts: 21
JPEG wrote:
Hi

NFPA 70E 130.7(C)(13)b) clearly says that a face shield without arc rating shall not be used. Now, when you buy one, the ATPV is clearly written on the face shield side.

I thought it was the same for coveralls but I can't find where it's written, if it is... Was it in NFPA 70E 2004?

So, is it a problem if someone buy a 8.2 cal/cm2 FR coverall and if this ATPV is not written on the coverall label?


NFPA 70E 130.7(C)(8) Table explains the standards of PPE conformance. Which describes in depth the different standards that relate to the variety of Personal protective Equipment.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883