It is currently Fri Nov 06, 2026 6:20 am
For 48Vdc battery systems, what voltage threshold do you use to require de-energizing?
50 Vdc 43%  43%  [ 13 ]
100 Vdc 20%  20%  [ 6 ]
something else 7%  7%  [ 2 ]
it depends 17%  17%  [ 5 ]
no DC 13%  13%  [ 4 ]
Total votes : 30
 Post subject: 50 Volt or 100 Volt threshold for DC?
PostPosted: Sun Jan 22, 2023 4:39 pm
OSHA and NFPA 70E Chapter 1 use 50 Volts as a threshold for requiring establishing an electrically safe work condition.
However 48V DC battery systems can have a float voltage upwards of 58 Volts DC.
...and NFPA 70E Article 320 Safety Requirements Related to Batteries and Battery Rooms sets the voltage threshold for batteries at 100 Volts DC. Chapter 3 can supplement or modify the requirements of Chapter 1.
With all that, here comes the question.
50 Vdc
100 Vdc
something else
it depends
no DC
 Post subject: Re: 50 Volt or 100 Volt threshold for DC?
PostPosted: Mon Jan 23, 2023 7:08 pm
I have met a few mechanics who are missing their ring finger. They forgot to disconnect the car battery before changing out a starter and their ring shorted out the power terminal on the starter to the frame or the engine. Instant anmputation. Always disconnect no matter what voltage.
