| Author: | mvann81 [ Mon Mar 14, 2011 9:51 am ] |
| Post subject: | 340.7 Power Electronic Equipment |
Upon reading Art. 340.7 (A) (6) it says that "circuit diagrams should be marked to indicate the hazardous component" How is everyone addressing this issue. At first glance, it would seem that all of our electrical schematics need anything hazardous (above 50 volt) marked with some type of indication that it is hazardous...that being said, they are electrical schematics and therefore 90% of the items on the schematics would need marked. Please advise on what everyone is doing to be in compliance. Thanks |
|
| Author: | jghrist [ Mon Mar 14, 2011 10:48 am ] |
| Post subject: | |
I would interprete this to mean only those hazards listed in 340.6. |
|