Hello everyone,

What do you assume for Hazard/Risk category for DC equipment over 600 Volts?

Also, how do you calculate DC Arc Flash hazards "D.8.1 Direct-Current Arc Flash Calculations" for voltages over 1000 Volts?

I'm currently working on an above 1000V system and trying to figure out what AF hazard level does this system pose.

Thank for you responses,

Marek


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jul 31, 2012 12:06 pm 
Offline
Sparks Level
User avatar

Joined: Wed Jun 10, 2009 5:00 pm
Posts: 204
Location: Toronto
DCAFA V2.0 software is applicable for systems with voltages in the range of 125 to 2000VDC, short circuit currents from 1 to 50kA, circuit time constants from 0 to 50msec.

_________________
Michael Furtak, C.E.T.
http://arcadvisor.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Aug 18, 2012 5:20 am 
Offline
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 1796
Location: North Carolina
You mean like those of us with electrostatic precipitators? I tried it a couple different ways. I used the formula in D.8.1 which is pretty simple. I also tried looking at the case of a drive and using the microfarads in the DC link capacitor, calculated the amount of energy stored in the drive under the assumption that the capacitor explodes for some reason (it does happen occasionally).

In all cases what I'm finding is that the assumptions used in the table (kA, fault time) are vastly higher than you ever encounter in real world cases. Even when I have DC motors in a Ward-Leonard loop with 8000 A maximum DC current outputs at 90 V DC, a full blown generator flashover never gets above 1.2 cal/cm^2 with the trip time that exists in this system. So what I'm finding is that the table is worthless...ignore it and do the real DC calculation. There was additional material presented at the IEEE ESW and PES conferences on this for quite some time but even if you assume silly stuff like battery series resistance of 0.01 ohms, you just can't get to 1.2 cal/cm^2 if you assume 2 second arcing time using the same logic which is clearly published in IEEE 1584.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883