Do the specific tasks listed in the work tables (130.7 c 15 a ) that are outside the scope of testing and trouble shooting require and Energized Work Permit or its equivalent ?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Oct 17, 2012 5:42 pm 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2174
Location: North Carolina
thehammer55 wrote:
Do the specific tasks listed in the work tables (130.7 c 15 a ) that are outside the scope of testing and trouble shooting require and Energized Work Permit or its equivalent ?


The task list and EEWP requirement are independent. You have to consider the risks (shock and arc flash) for ALL tasks. The EEWP is only an administrative control to minimize exposure to the risks to those that are actually necessary. OSHA has a lot more to say about when it is appropriate. Read the letters of interpretation for the corresponding OSHA 1910.3xx.