ekstra   ara
 Post subject: disconnects
PostPosted: Sat Mar 16, 2013 1:29 pm 
Offline

Joined: Sat Mar 16, 2013 6:29 am
Posts: 4
Can a operator in a (3phase 480 system) be allowed to turn a non-fusible water tight disconnect off to motor?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Mar 17, 2013 12:00 pm 
Offline
Arc Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 679
Location: Rutland, VT
What is the arc flash hazard for that disconnect? Does the operator have the correct PPE for the arc flash hazard? Has he been trained to read and understand what is on the arc flash hazard label?

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Mar 18, 2013 3:42 am 
Offline

Joined: Sat Mar 16, 2013 6:29 am
Posts: 4
Motor will not engerize without going thur a squence to start. No training for the operator or ppe. When replacing nozzles on seperators, they pull the machine apart. Lock out 5 or 6 disconnects on differnt motors to have system locked out. No flash arc tags on disconnects. If they can do this on 480, why can t they do a disconnect on a homginzer with a tag. Same 480 system(same amp draw-200,250, at start up) all frq drives in another panel-100ft away upstairs.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Mar 18, 2013 4:54 am 
Offline
Arc Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 679
Location: Rutland, VT
Is the line side of the disconnect still energized when it is in the off position? Is this disconnect between a variable drive and the motor? Makes a difference is operation but do you still have to test for de-energization prior to working on motor or just try to start it?

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Mar 18, 2013 7:24 am 
Offline
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 439
Location: Wisconsin
wes hardin wrote:
Motor will not engerize without going thur a squence to start. No training for the operator or ppe. When replacing nozzles on seperators, they pull the machine apart. Lock out 5 or 6 disconnects on differnt motors to have system locked out. No flash arc tags on disconnects.

Many companies have 'mechanical' LOTO procedures that cover this situation which do not require PPE. Their reasoning is based on the frequency of operation of the disconnects means they are 'properly maintained' and that this specific operation is 'not likely to cause an arc flash'.
If the operator is trained in this operation, per OSHA they are qualified. Your Safe Work Practices program is between your company, OSHA, and the US legal system. NFPA70E does not specifically prohibit this procedure.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Mar 18, 2013 2:08 pm 
Offline

Joined: Sat Mar 16, 2013 6:29 am
Posts: 4
wbd wrote:
Is the line side of the disconnect still energized when it is in the off position? Is this disconnect between a variable drive and the motor? Makes a difference is operation but do you still have to test for de-energization prior to working on motor or just try to start it?

yes, the disconnect is between the freq drive and motor. No pre -test to see if motors start. If have to select what product u are running and what tank you are coming from and going to. A squence (program ) is pulled down to start system. Disconnects have feed -back on them and will not let program start. wes


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Mar 18, 2013 2:14 pm 
Offline

Joined: Sat Mar 16, 2013 6:29 am
Posts: 4
JBD wrote:
Many companies have 'mechanical' LOTO procedures that cover this situation which do not require PPE. Their reasoning is based on the frequency of operation of the disconnects means they are 'properly maintained' and that this specific operation is 'not likely to cause an arc flash'.
If the operator is trained in this operation, per OSHA they are qualified. Your Safe Work Practices program is between your company, OSHA, and the US legal system. NFPA70E does not specifically prohibit this procedure.

I see now , where u are coming from. Since the power is off to the disconnect, unless the drive is on, should be no hazard,unless turned off while drive is on and motor running.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 7 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883