Hello All,

I have just received my copy of NFPA 70E-2009 and have a couple of questions about changes and outstanding issues I hope someone will be kind enough to help me with.

1) I see 130.3 Exception No. 1 was added to better align with IEEE 1584. I also see many people are assuming this to mean HRC = 0. Any ideas how that aligns with Table 130.7(C)(9) which has a few tasks at HRC 1 with <= 240 V rated equipment.

2) Is a lab coat-style AF clothing "legal" for any HRC level with nothing more than natural fiber clothing underneath?

3) Any idea on the rationale behind the hearing protection? Possibly due to the arc blast?

Thank you in advance.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jan 20, 2009 7:37 am 
Offline
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
MIEngineer wrote:
1) I see 130.3 Exception No. 1 was added to better align with IEEE 1584. I also see many people are assuming this to mean HRC = 0. Any ideas how that aligns with Table 130.7(C)(9) which has a few tasks at HRC 1 with <= 240 V rated equipment.


Apples and oranges. Use the tables or the analysis, the assumptions are different.

MIEngineer wrote:
2) Is a lab coat-style AF clothing "legal" for any HRC level with nothing more than natural fiber clothing underneath?


No, you have to have full coverage, if you use a "lab coat" you need the leggings also. Arcs do very strange things, they dont do the same thing twice. See the videos here for some good examples. http://www.westexinc.com/

MIEngineer wrote:
3) Any idea on the rationale behind the hearing protection? Possibly due to the arc blast?


Yes, the pressure form the blast can rupture eardrums, this requirement has nothing to do with burn protection, the hearing protection is always covered with a hood or head sock for that.

Thank you in advance.[/QUOTE]


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Jan 21, 2009 6:06 pm 
Offline
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 427
A recent class showed the result after flashing a dummy with lab coat and leggings. The flash blew up in between, leaving the dummy with a burned crotch.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883