RobertDrew wrote:
Jim, your response points out a hole in my understanding of AF. What ties IEEE 1584 calcs to 70E currently?
Great question. Although there is no direct mandate to use IEEE 1584 as part of NFPA 70E requirements (NFPA 70E PPE Category Tables are another option), it is the main standard used globally to calculate the incident energy/working distance and arc flash boundary.
NFPA 70E 130.5 Defines when and how to perform an arc flash risk assessment. This may include an incident energy analysis and arc flash boundary (PPE Category Tables are the other option)
130.5(D) Incident Energy Analysis and
130.5(G) Arc Flash Boundary both reference Annex D. The 2002 edition of IEEE 1584 has been in
Annex D since the 2004 Edition of NFPA 70E.
The results of the arc flash calculations may also be listed on an energized electrical work permit
(NFPA 70E 130.2(B)(2)) as well as equipment (arc flash) labels
(NFPA 70E 130.5(H)). IEEE 1584 is referenced in
Table 130.5(C) Estimate of the Likelihood of Occurrence of an Arc Flash Incident for ac and dc Systems
Informational Note No. 6.So, IEEE 1584 and NFPA 70E are somewhat intertwined when it comes to electrical safety.