 Post subject: DC Arc Flash
PostPosted: Fri Oct 31, 2014 5:13 am 
Offline
Arc Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 683
Location: Rutland, VT
Hello,

I have been thinking about the ramifications of the DC Arc Flash Table 130.7(C)(15)(B) for a 125V, 60 cell, battery bank that is typical for generating stations and large substations. Yes, I know that installations under the control of utilities are not covered but this seems to be the only standard/consensus document that has DC arc flash in it.

Typically with the arrangement for 60 cells the positive connection is on one end and the negative connection on the other end or on a level below depending on how many tiers. Many battery inspections consist of a monthly bank voltage reading with a multimeter.

Now for a 125Vdc, 60 cell, 670 Ah battery the manufacturer's spec sheet has a short circuit current of 8,840 A. Using the table above, this results in a Arc Flash PPE Category of 3 and Table 130.7(C)(15)(A)(a) indicates that Arc Flash PPE is needed for voltage testing on series connected battery cells.

Considering the distance between the positive terminal and the end negative terminal, standard voltage leads supplied with a multimeter may not reach so many people have auxiliary leas made up to span the distance. Given that the risk of shorting out the entire battery bank with a multimeter with extremely small wire seems unlikely, isn't the PPE class of 3 a little extreme?

Thoughts?

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 1 post ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883