 Post subject: 130.3 Ex.1 (2) The circuit is supplied by one Transformer.
PostPosted: Mon Jul 20, 2015 12:01 pm 

Joined: Mon Jul 20, 2015 11:47 am
Posts: 2
I am reviewing an Arc Flash study.
The Utility is using three single 25kva transformers
for a 75kva 240v delta transformer bank.
Will this installation meet NFPA 70 E Article 130.3 Exception 1?
Are the three single phase transformers provided by the Utility ,
meeting the intent of Paragraph (2)?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: 130.3 Ex.1 (2) The circuit is supplied by one Transform
PostPosted: Mon Jul 20, 2015 4:06 pm 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 524
Location: Wisconsin
rsuhadolc wrote:
I am reviewing an Arc Flash study.
The Utility is using three single 25kva transformers
for a 75kva 240v delta transformer bank.
Will this installation meet NFPA 70 E Article 130.3 Exception 1?
Are the three single phase transformers provided by the Utility ,
meeting the intent of Paragraph (2)?


The exception you mention was last seen in 2009, you really should get a new copy of NFPA70E
This exception also does not exist in the previous version (2012) of NFPA70E. Instead there is a recommendation to look at IEEE1584 for transformers <240V.

So in summary:
Yes three interconnected single phase transformers units are considered to be the same as a single 3-phase transformer. The prohibition is against paralleled 3-phase transformers.
240V secondary transformers need to be considered.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: 130.3 Ex.1 (2) The circuit is supplied by one Transform
PostPosted: Tue Jul 21, 2015 7:49 am 

Joined: Mon Jul 20, 2015 11:47 am
Posts: 2
We will review again with NFPA 70 E 2015 Table 130.7 (C) (15)(A)(b)


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: 130.3 Ex.1 (2) The circuit is supplied by one Transform
PostPosted: Tue Jul 21, 2015 9:46 am 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 825
Location: Rutland, VT
rsuhadolc wrote:
We will review again with NFPA 70 E 2015 Table 130.7 (C) (15)(A)(b)


I noticed in your original post you mentioned you are reviewing an arc flash study. That implies an actual was done using IEEE 1584 methodology. Therefore, the incident energy levels should have been calculated and therefore you cannot use the NFPA Table mentioned above. See NFPA 70E-2015 130.5(C)

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883