Forum members,

In reviewing the defined parameters of Table 130.7(C)(15)(A)(b), I noted that several of the Equipment parameters requiring Category 1 and 2 PPE don't seem real-world. The requirement that the maximum clearing time be 2 cycles (0.03 sec) seems like it would only apply to fuse protection and not to a molded case circuit breaker (other than some type of smart breaker). I am wondering if the Equipment parameters noted in these instances are actually only referring to fuse protection, and if so, I think it might be best to stipulate.

I would appreciate your input,


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Defined Parameter Tables and validity
PostPosted: Thu Sep 03, 2015 5:52 pm 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2178
Location: North Carolina
Small molded case breakers (generally under 100 A) typically operate in 1-2 cycles so nothing wrong with the entries at all. It's only when you get into the larger frame sizes where the physical movement becomes a limiting factor that clearing times extend out to 3-5 cycles, or even up to 10-12 cycles for older breakers and a lot of higher voltage SF6 breakers. That's one of the major benefits of vacuum interrupters for higher voltages and currents...the physical contacts only move about 1/4 to 3/8" and once they separate at the next current zero crossing, the arc clears so typical specifications list 3 cycles for opening time with vacuum. I wouldn't even bother with a Limitamp or similar air breaker for medium voltage or over 800 A frames.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883