Hello All,

Table 130.7(C)(9) gives me a good start for FR clothing requirements until I have a full study done. Once I have completed a full study then there are no longer different Hazard/Risk catergories on the same piece of equipment?

To clarify:
A Panelboard <240V has category 0 & 1 requirements based on the task according to 130.7(C)(9). Once my arch flash study indicates category 0 incident energy available then ANY task requires category 0 PPE, correct? Everything from CB operation to work on energized conductors?

Thank you,


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Mar 25, 2009 5:51 am 
Offline
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
MIEngineer wrote:
Hello All,

Table 130.7(C)(9) gives me a good start for FR clothing requirements until I have a full study done. Once I have completed a full study then there are no longer different Hazard/Risk catergories on the same piece of equipment?

To clarify:
A Panelboard <240V has category 0 & 1 requirements based on the task according to 130.7(C)(9). Once my arch flash study indicates category 0 incident energy available then ANY task requires category 0 PPE, correct? Everything from CB operation to work on energized conductors?

Thank you,


Close, once you do the study you need to wear PPE rated for your calculated Ei, you no longer use the HRC. You are correct about the tasks, it will all be the same as long as they are working at or beyond the estimated working distance.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883