 Post subject: Older Labels with both incident energy and Category PPE list
PostPosted: Wed Apr 06, 2016 9:36 am 
Sparks Level

Joined: Tue Jan 19, 2010 2:35 pm
Posts: 175
I'd like to get your input. Labels produced using the older versions of the NFPA 70E listed both PPE category as well as calories. For example a label could say 4.5 calories per square centimeter plus Category 2 PPE. The issue is the new standard prohibits listing both.
So my question is: Do you think it's necessary to update older labels so that only one of the two is listed? Please assume that nothing has changed in the facility so the electrical system is the same as when the study was done.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Older Labels with both incident energy and Category PPE
PostPosted: Wed Apr 06, 2016 9:54 am 
Sparks Level
User avatar

Joined: Tue Nov 12, 2013 6:31 am
Posts: 238
Location: Port Huron, Michigan
wilhendrix wrote:
I'd like to get your input. Labels produced using the older versions of the NFPA 70E listed both PPE category as well as calories. For example a label could say 4.5 calories per square centimeter plus Category 2 PPE. The issue is the new standard prohibits listing both.
So my question is: Do you think it's necessary to update older labels so that only one of the two is listed? Please assume that nothing has changed in the facility so the electrical system is the same as when the study was done.


You don't need to change labels that are still valid. As you do put new labels out, you'll want the new labels to list the incident energy. You can add in a site specific classification for the PPE needed, which can coincidentally happen to have the same number designation as the tables method.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883