 Post subject: Table 130.7(C)(15)(A)(a) was deleted in the 2018 70E edition
PostPosted: Sun Nov 04, 2018 4:37 pm 

Joined: Fri May 30, 2014 4:37 pm
Posts: 2
Why was Table 130.7(C)(15)(A)(a) deleted in the 2018 70E edition?
I found it very useful


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Table 130.7(C)(15)(A)(a) was deleted in the 2018 70E edi
PostPosted: Mon Nov 05, 2018 5:24 am 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 881
Location: Rutland, VT
The Foreword in NFPA 70E-2018 states the reason that table in 2015 was modified to determine the likelihood that an arc flash could occur and was renumbered to Table 130.5(C), so refer to that table and it has basically the same info you are looking for.

Always a good idea to read the foreword as changes are discussed there.

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com