 Post subject: NFPA 70E 2024 Hair Nets
PostPosted: Tue Nov 28, 2023 12:51 pm 

Joined: Tue Jun 14, 2022 11:35 am
Posts: 17
In the latest addition of NFPA 70E, 130.7(C)(3), the last sentence states that "If employees use hairnets or beard nets, or both, these items shall be arc rated". Does this mean that if you have a panel that is <1.2 ca/cm2 that the hair nets still need to be arc rated?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: NFPA 70E 2024 Hair Nets
PostPosted: Wed Nov 29, 2023 8:24 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 624
Effectively, yes. Unless you can find non-arc-rated nets that meet 130.7(C)(11). Also see (12). It should be noted that non-arc rated meltable fabrics have not been tested to 1.2 or any other IE level. Even if you were to have a batch tested, there would be nothing to stop a manufacturer from changing the formula between batches.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: NFPA 70E 2024 Hair Nets
PostPosted: Thu Nov 30, 2023 12:39 pm 

Joined: Tue Jun 14, 2022 11:35 am
Posts: 17
stevenal wrote:
Effectively, yes. Unless you can find non-arc-rated nets that meet 130.7(C)(11). Also see (12). It should be noted that non-arc rated meltable fabrics have not been tested to 1.2 or any other IE level. Even if you were to have a batch tested, there would be nothing to stop a manufacturer from changing the formula between batches.


Isn't C11 & 12 referring to when arc rated clothing is required? If I am in a control cabinet that is .25 cal/cm2 and troubleshooting, would the arc rated hair net apply?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: NFPA 70E 2024 Hair Nets
PostPosted: Thu Nov 30, 2023 1:25 pm 
Sparks Level

Joined: Thu Apr 18, 2019 11:42 am
Posts: 132
I think that really is a company's, risk assessed decision.

Mike


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: NFPA 70E 2024 Hair Nets
PostPosted: Mon Dec 04, 2023 9:04 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 624
If C(11) and C(12) were only referring to when arc rated clothing was required, there would be no need for most of the language provided in those sections.
Also, don't forget the OSHA general duty clause.

The task mentioned appears to fit in Table 130.5(C) under the "likely" category.

What exactly is the downside of wearing an arc-rated net for this task, or even making it part of your daily uniform?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: NFPA 70E 2024 Hair Nets
PostPosted: Tue Dec 05, 2023 1:52 pm 

Joined: Tue Jun 14, 2022 11:35 am
Posts: 17
stevenal wrote:
If C(11) and C(12) were only referring to when arc rated clothing was required, there would be no need for most of the language provided in those sections.
Also, don't forget the OSHA general duty clause.

The task mentioned appears to fit in Table 130.5(C) under the "likely" category.

What exactly is the downside of wearing an arc-rated net for this task, or even making it part of your daily uniform?



When we do an AF study and and get the incident energy values we don't base it on whether it is likely to occur or not, only if it happens this is what the hazard will be.

If you have a panel with a 7 cal/cm2 label and used Table 130.5(C) and it said no likelihood, would you tell your employee not to wear arc flash PPE?

The downside has two parts, one from a cost perspective AR hair nets and beard nets are expensive and are treated like a disposable item vs being laundered like a uniform. The other is lines in 70E like the last sentence of 130.7(C)(3) create confusion for workers who have to use PPE and safety professionals that have to create rules and procedures in manufacturing. We tell workers that less than 1.2 cal/cm2 no arc rated PPE is required but then say you must wear arc rated hair nets if they are required.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: NFPA 70E 2024 Hair Nets
PostPosted: Wed Dec 06, 2023 8:13 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 624
Win wrote:
If you have a panel with a 7 cal/cm2 label and used Table 130.5(C) and it said no likelihood, would you tell your employee not to wear arc flash PPE?
No.

Under 1.2, are non-arc rated nylon shirts and polyester pants are okay for workers to wear?


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 7 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883