Does a mobile generator (400kva) require a short-circuit current/incident energy assessment. If it does what reference or standard require a decal or study to be performed. I am caught in the middle between a customer and manufacture. I have to prove what standard require an assessment to be performed doesn't matter if the generator is used in a temporary or permanent installation.

Please help!!


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Generator Arc Flash Requirements
PostPosted: Sat Aug 31, 2024 5:44 am 

Joined: Sat Aug 31, 2024 5:40 am
Posts: 1
Location: Chile
sgibson@multiquip.com wrote:
Does a mobile generator (400kva) require a short-circuit current/incident energy assessment. If it does what reference or standard require a decal or study to be performed. I am caught in the middle between a customer and manufacture. I have to prove what standard require an assessment to be performed doesn't matter if the generator is used in a temporary or permanent installation.

Please help!!


Hello! Did you find a solution for this?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Generator Arc Flash Requirements
PostPosted: Tue Sep 03, 2024 7:27 am 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 619
Location: Wisconsin
There is no US code requiring Arc Flash Incident Energy labeling.
NFPA70E is the typical standard required to comply with customer contractual language as well as for governing agencies, like OSHA.

So the answer is:
What does your contract with the customer say.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883