Arc Flash Forum
NFPA 70E 2009 table
https://brainfiller.com/arcflashforum/viewtopic.php?f=7&t=598
Page 1 of 1
Author:  J.T [ Fri Jul 24, 2009 10:00 am ]
Post subject:  NFPA 70E 2009 table
I have NFPA 70E 2004. I want to compare the table 130.7(c)(9)(a) of 2004 with the one of 2009 edition. Can someone post the table 130.7(c)(9)(a) of 2009?
Author:  Zog [ Fri Jul 24, 2009 10:46 am ]
There are a ton of changes in both ths stanrard and the tables, and the 2009 is in effect so I suggest you get the whole 2009 standard.
If you have a more specific question I will be glad to answer it, one of the more major changes to the tables is all breaker racking operations, LV and MV, doors open or closed now require HRC 4.
Author:  stevenal [ Mon Jul 27, 2009 11:23 am ]
[url="http://nfpaweb3.gvpi.net/rrserver/browser?title=/NFPASTD/70E09"]http://nfpaweb3.gvpi.net/rrserver/browser?title=/NFPASTD/70E09[/url]
Author:  elihuiv [ Wed Aug 26, 2009 2:51 am ]
2009 Table Changes
Most of the table changes are small bumps up in HRC for MCC work.
The footnotes also changed to eliminate the "low fault current" lessening of PPE and to fix the issues that were in the TIA. Steve's post above me gives the 2009 online so you can read it. NFPA offers this but you can't search or cut and paste.
If you are in Toronto you will now fall under CSA Z462 and you can read it online at http://www.CSA.org and you can purchase PDF's there too.
Author:  Vincent B. [ Wed Aug 26, 2009 1:11 pm ]
The correct URL for the Canadian Standards Association is http://www.csa.ca, and you can buy their standards at http://www.shopcsa.ca. I'm not aware of a view-only online version of CSA Z462: do you have a URL/menu navigation for it?
http://www.phpbb.com/