brainfiller wrote:
I believe most (all?) software also use this interpretation.
In case it may help someone else, I'll note that at least one software is having some trouble with applying the 85% correctly based on voltage.
The SynerGEE software v3.8.3.153 by GL (formerly Advantica) calculates arcing current at both 85% and 100%, but the summary report only displays the resulting incident energy that is greatest, so it could be from the 85% or 100% value, which is okay for <1kV, but not expected for >1kV. There is a separate report to see the details, the problem is with the summary report.
Another problem is that the software appears to have an option to modify the reduced arcing current from 85% to any specified value, but this setting does not actually do anything at this time. You would think that you could force the calcs to 100% using this setting when studying >1kV, but it currently does nothing.