I am performing an arc flash analysis for my company and I have noticed that the IEEE 1584 calculations require the use of "bolted fault current". How is this calculated and is there a site that goes further into explaining how to calculate this value?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Jul 22, 2011 11:29 pm 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
Bolted fault current is just the normally calculated fault current with no fault impedance. IEEE Red Book Std 141 is a good source for calculations, but there are many good sources. IEEE Std 1584 comes with a Bolted Fault Current Calculator Excel spreadsheet.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Jul 25, 2011 10:53 am 
User avatar

Joined: Sun Jul 13, 2008 5:00 pm
Posts: 24
The Red Book is a great resource. There is also a newer IEEE standard:

551-2006 - IEEE Recommended Practice for Calculating AC Short-Circuit Currents in Industrial and Commercial Power Systems.

It's referred to as the Violet Book.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jul 26, 2011 1:50 pm 

Joined: Wed Aug 06, 2008 9:19 am
Posts: 3
tdriller wrote:
I am performing an arc flash analysis for my company and I have noticed that the IEEE 1584 calculations require the use of "bolted fault current". How is this calculated and is there a site that goes further into explaining how to calculate this value?


Umm, if bolted fault current calculations are a question, you might need help performing the arc flash study.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jul 26, 2011 3:03 pm 

Joined: Fri Sep 25, 2009 5:00 pm
Posts: 43
This is actually easier than you might imagine. The software that is used to perform the arc flash study can also perform the bolted short circuit calculations using the same data base. I'm not sure if every program does, but all the major ones do.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Dec 06, 2011 7:28 am 

Joined: Tue Dec 06, 2011 7:19 am
Posts: 1
Kim L. wrote:
Umm, if bolted fault current calculations are a question, you might need help performing the arc flash study.


Umm............ Maybe that's why he is here asking for help? Just sayin'


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Dec 07, 2011 10:16 am 
Sparks Level
User avatar

Joined: Sat Jun 07, 2008 5:11 pm
Posts: 143
Location: Connecticut
Check the Cooper Electric website... a good source of info. Also there are a number of free Excel spreadsheet programs on the net.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 7 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883