 Post subject: What is the range of E and En?
PostPosted: Wed May 27, 2009 6:28 pm 
Offline

Joined: Wed May 27, 2009 6:02 pm
Posts: 3
Hi:
Would you please help to get the expected value for E & En for 480V in-box switchgear? We were trying to use the IEEE 1584 formula
Log En = K1 + K2 + 1.081 * Log Ia + 0.0011 * G AND
E = 4.184 * Cf * En * (t/0.2) * (610^x/D^x).

I (bolted fault) = 40kA.

If we got Log En = 515, would that be correct? and what is En?

Thanks,
abbhas2009


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu May 28, 2009 12:22 am 
Offline
Sparks Level
User avatar

Joined: Mon Jul 09, 2007 11:43 pm
Posts: 51
Location: Sheffield, England
Good to see somebody using the calculations long hand (manually). En is the normalized Incident Energy for an arc duration of 0.2 seconds and for a distance of 610mm. The second equation that you show is to adjust this normalized figure to the actual duration and the actual distance to the worker. I'm not sure where your figure of 515 comes from for Log En, seems very big to me. I suspect that you've not considered that the K factors are negative numbers or perhaps you've misplaced a decimal point somewhere. If you log onto the link below, Jim Phillips provides really easy step by step work sheets for the calculation of arcing current, incident energy and flash protection boundaries. (They are free plus lots of other very useful material as well)

http://www.brainfiller.com/newsletterArchive.php


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu May 28, 2009 9:01 am 
Offline

Joined: Wed May 27, 2009 6:02 pm
Posts: 3
What are the values of E and En?

Hi Mike,

Thank you, we had considered the minus, however, the voltage was incorrect (480 was corrected to 0.48). The new result for Log En, En and E is 0.77, 5.93 and 3.72 respectively.

When we changed the bolted fault current to 106kA, the results got higher a little up to 1.15, 14.27 and 8.98.

E: in J/cm^2

Have a nice day,
abbhas2009


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu May 28, 2009 9:11 am 
Offline
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 409
Location: Spartanburg, South Carolina
You haven't shown the calculation of Ia (arcing current) from Ibf (bolted fault current) using IEEE-1584 Equation (1).

I can't get your numbers using either the arcing current or the belted fault current.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu May 28, 2009 12:19 pm 
Offline

Joined: Wed May 27, 2009 6:02 pm
Posts: 3
Values for En and E

Hi jghrist;

It is the same equation for IEEE 1584. We believe that the values are coming reasonable.

Regards,
abbhas2009


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883