 Post subject: IEEE 1584-2018 - Annex D
PostPosted: Fri Jan 18, 2019 12:04 pm 
User avatar

Joined: Fri Jan 18, 2019 11:47 am
Posts: 2
Hello all,

I have a specific question in context to the new IEEE 1584-2018 - IEEE Guide for Performing Arc-Flash Hazard Calculations’ standard.

There are a couple of equations in Appendix - D, equation numbers "(D.101)" and "(D.104)" in pdf page number 74.

In both these equations (D.101 and D.104), they specify a term 'k3*Iarc_600' in the numerator and calculated the final values with respect to it, whereas I believe that it should actually be calculated with respect to "k3*Iarc_600_min".

If someone, who has already looked into the standard or willing to look into it now, comment on my understanding, it will be very useful.

Regards,
Balaji Prabhakaran (MIET) | Senior Power Systems Engineer
British Power International


Last edited by wbd on Sat Jan 19, 2019 5:38 am, edited 1 time in total.
removed personal contact info


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: IEEE 1584-2018 - Annex D
PostPosted: Sun Jan 20, 2019 3:48 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1504
Location: Scottsdale, Arizona
The 2018 Edition of IEEE 1584 has quite a bit there. Nothing like the 2002 Edition.

D.101 is equation 6 from 4.6 of the standard.
D.104 is equation 10 from 4.7 of the standard.

I hope that helps clarify a bit.

Best Regards,
Jim


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: IEEE 1584-2018 - Annex D
PostPosted: Tue Jan 22, 2019 3:37 am 
User avatar

Joined: Fri Jan 18, 2019 11:47 am
Posts: 2
Hello Jim,

Thanks very much for your response.

However, 4.6 mentions about a general equation '(6)' that must be used for both intermediate and minimum 'E' calculation. However, '(D.101)' is specific to calculating minimum 'E' and hence you will notice 'K13*log(Iarc_min)' used in '(D.101)' in the place of 'K13*lg*Iarc' in equation '(6)'. Therefore, I still believe that it should actually be calculated with respect to "k3*Iarc_600_min".

Please comment/clarify.

Regards,
Balaji Prabhakaran (MIET) | Senior Power Systems Engineer
British Power International

_________________
Let Peace Be!
Balaji


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883