The secondary bushings are all in line, horizontal for the phases as opposed to staggered or offset, and much closer spaced than in a pad mount without a breaker.

What would you call this configuration? HCB?

Attachment:
1000 kva with breaker.jpg
1000 kva with breaker.jpg [ 1.74 MiB | Viewed 144404 times ]


Attachment:
1000 kva with breaker bus.jpg
1000 kva with breaker bus.jpg [ 1.03 MiB | Viewed 144404 times ]

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Pad mounted transformer with secondary breaker
PostPosted: Wed Mar 27, 2019 4:58 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 499
Just for grins, here's another one I just bought for my work. More standard configuration with the breaker cable fed.

Attachment:
500 kva with breaker 1.jpg
500 kva with breaker 1.jpg [ 1.18 MiB | Viewed 144401 times ]


Attachment:
500 kva with breaker 2.jpg
500 kva with breaker 2.jpg [ 1.28 MiB | Viewed 144401 times ]

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Pad mounted transformer with secondary breaker
PostPosted: Mon Apr 01, 2019 7:13 am 
Sparks Level

Joined: Sat Apr 04, 2009 9:50 pm
Posts: 122
Location: San Antonio, TX
In my opinion, the first configuration is Hcb. The second is VCBB.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Pad mounted transformer with secondary breaker
PostPosted: Mon Apr 01, 2019 11:06 am 

Joined: Mon Nov 24, 2008 6:42 pm
Posts: 5
Location: Nashville, TN
I agree. First one is HCB, second is VCBB.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Pad mounted transformer with secondary breaker
PostPosted: Fri Apr 05, 2019 11:32 am 
Sparks Level
User avatar

Joined: Tue Oct 26, 2010 5:00 pm
Posts: 201
Location: Maple Valley, WA.
I too agree. HCB for the first photo and VCBB for the second.

_________________
Robert Fuhr, P.E.; P.Eng.
PowerStudies


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883