PostPosted: Fri Jun 26, 2009 8:33 am 
Offline
Sparks Level

Joined: Wed May 13, 2009 3:19 pm
Posts: 56
I would like some comments on how others have handled, in our opinion, the unrealistic flash boundaries the 1584 methodology can produce. We have many locations with both large fault currents and potentially long clearing times or the FCT is clamped at 2 seconds due to several factors. These locations often return a very very large flash boundary. We are having issues with putting numbers over 30’ on a label much less numbers that are over a hundred feet. Our goal is to make sure the site take the results seriously but when the flash boundary is outside the gate people tend to ask questions. We are considering using a maximum flash boundary but are unsure of what this distance should be. Has anyone else established a maximum flash boundary? If so, what number did you use and what was your justification? If not, how have you discussed the extreme distances with your site or clients? What was their reaction? Thank you.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Jun 26, 2009 8:50 am 
Offline
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
SCGEng1 wrote:
I would like some comments on how others have handled, in our opinion, the unrealistic flash boundaries the 1584 methodology can produce. We have many locations with both large fault currents and potentially long clearing times or the FCT is clamped at 2 seconds due to several factors. These locations often return a very very large flash boundary. We are having issues with putting numbers over 30’ on a label much less numbers that are over a hundred feet. Our goal is to make sure the site take the results seriously but when the flash boundary is outside the gate people tend to ask questions. We are considering using a maximum flash boundary but are unsure of what this distance should be. Has anyone else established a maximum flash boundary? If so, what number did you use and what was your justification? If not, how have you discussed the extreme distances with your site or clients? What was their reaction? Thank you.


Wireless remote racking and operators.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Jun 26, 2009 9:25 am 
Offline
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1207
Location: Scottsdale, Arizona
That is one of the "holes" in IEEE 1584. As you already found out, lower short circuit currents can produce long clearing times and the equations treat this the same as a high short circuit current and low clearing time. Other than the 2 second cut off which can still produce very large results, there is not much else in writing.

The newer reseach is lookng at arc extinction times since the arc might extinguish long before a device trips.

I was just in the lab this week "blowin stuff up" :eek: fpr some independent testing and we had a hard time gettting a 30 kA bolted / 15 kA arcing current to sustain more than 1 or 2 cycles. It was phase-to-ground testing. Three phase sustained quite well - we even managed to throw a bus bar placed on top of the phases about 20 feet with that low of current.

There is still a possibility for some equipment that a phase-ground arc flash can go three phase quickly.

With all that said, there really is not a good answer yet. I understand the new IEEE / NFPA testing might finally be looking at energy per time which is what it will take to distinguish between incident energy from low current / long clearing time and high current / low clearing time.

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jun 30, 2009 6:40 am 
Offline
Sparks Level

Joined: Wed May 13, 2009 3:19 pm
Posts: 56
Thank you for the response, we look forward to more research and testing not only on this subject but many of the other arc flash “gray areas” at well.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883