Ashdgee wrote:
Hello all,
I trust you are all well.Going through the sample calculations provided in this new standard.While I'm waiting for the new software to be purchased by our firm ,I'm currently using excel spreadsheets (which is more laborious of course) for now.
For those of you who went through the sample calculations provided within the IEEE 1584-2018, whether you used software or manual methods (excell etc), are your values coming out matching those provided in the standard ?
Most of my values are coming out quite correct , except they are a bit higher towards the end i.e the stage of recalculating the arc flash boundary and incident energy based on the reduced arcing current.I'm referring to the example of the 480V system , where my incident energy is around 65 J/mm instead of 53 J/mm as shown on the standard.
Have any of you gone through those sample examples on your own and obtained similar values as ones in the stanmdard? Just want to know whether I am wrong or not, although I have double checked numerous times.
Regards
Ashford
yes the values are coming out matching those provided in the standard.