It is currently Sun Apr 11, 2021 8:32 am



Post new topic Reply to topic
Author Message
ekstra   ara
 Post subject: IEC 61641 "Arc Free" vs NFPA 70E / IEEE 1584
PostPosted: Sat Mar 20, 2021 5:15 pm 

Joined: Fri Jan 15, 2016 12:45 pm
Posts: 1
All,

I'm posting this here as it is really this new question of IEC 61641 in my North American world of NFPA 70E/IEEE 1584. I've done various studies based on the latter for my US clients.

To the best of my knowledge, North American standards like NFPA 70E and IEEE 1584 regarding arc flash have no equivalent to IEC 61641 for "arc ignition protected zones". I understand the IEC used to refer to this as "arc free".

In Section 1 (Scope) of the IEC 61641, it ends with the sentence, "This is a voluntary test made at the discretion of the manufacturer." At the very end of the standard in Annex B, it has this very curious note (that is suggested to need inserted right after the Section 1 last sentence):

"NOTE 2 The recommendations of this report are not acceptable in the USA, nor in Canada, nor in the United Kingdom."

Can anyone speak to why this was inserted. I have seen some misgivings in posts elsewhere regarding IEC 61641. This note appears to have actually written into the standard some sort of significant split. I can't help wonder if it is the "arc ignition protected zones" versus the rest of the standard's testing to something similar to IEEE C37.20-7.

Thanks in advance for any potential help.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: IEC 61641 "Arc Free" vs NFPA 70E / IEEE 1584
PostPosted: Mon Mar 22, 2021 8:03 am 
Sparks Level

Joined: Thu Jul 07, 2011 6:03 am
Posts: 66
Location: Netherlands
First: I don't know the exact reason why it has been inserted in that way. My guess is that the standard, like IEC 61439 for LV switchgear, is performance based and doesn't specify any design parameters like ANSI standards. As long as the tests are passed it doesn't matter *how* they were passed and that could be a reason the standard has not been adopted in these jurisdictions.

The benefits of arc ignition protection zones are fairly limited as the testing conditions (such as closed panel doors) typically fall under the "no likelihood of occurence" in NFPA 70E Table 130.5(C). Work that happens where the testing conditions are invalidated, for example after opening a door or removing a barrier to do voltage testing, still require a risk assessment like for any other type of switchgear. So the hazard is the same, the likelihood of occurrence is lower for conditions that already had a low likelihood. You would need a very mature and detailed electrical safety program for this to make a meaningful difference in working procedures.

There are useful exceptions like LV switchgear that maintains the arcing class while racking breakers but I've never seen those in the wild.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours