When using IEEE 1584 Table 4, does an overhead switch on a utility 12.47 kV distribution circuit fall under the open air category or the switchgear category?

I figure that open air is applicable and that switchgear is intended for enclosed type equipment, which this is not.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Jul 09, 2009 6:59 pm 
Sparks Level

Joined: Sun Dec 23, 2007 1:44 pm
Posts: 348
Location: Charlotte, NC
If it is an open air break switch, then it shoud be analyized as open air.

Alan


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Jul 09, 2009 7:02 pm 
Sparks Level

Joined: Sun Dec 23, 2007 1:44 pm
Posts: 348
Location: Charlotte, NC
And if it is utility owned open air equipment, I would use Arcpro and not 1584 for the numbers.

Sorry for the double post.

Alan


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Jul 10, 2009 4:56 pm 

Joined: Wed Jun 24, 2009 4:45 pm
Posts: 41
Location: WA State
acobb wrote:
And if it is utility owned open air equipment, I would use Arcpro and not 1584 for the numbers.

Sorry for the double post.

Alan


Can you please explain why the preference for Arcpro?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Jul 11, 2009 5:58 am 
Sparks Level

Joined: Sun Dec 23, 2007 1:44 pm
Posts: 348
Location: Charlotte, NC
The open air calcs for over 1000 volts in 1584 assume a 3 phase fault. The NESC treats everything as a single phase fault because of the larger phase spacings. Arcpro was used to create the tables in the NESC and models single phase arcs in open air. We only use 1584 for enclosures and voltages less than 1000 volts.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Jul 13, 2009 7:13 am 

Joined: Wed Jun 24, 2009 4:45 pm
Posts: 41
Location: WA State
Great feedback, thank you very much!


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883