Aestrick
|
Post subject: Arc flash for <125 kVA transformers Posted: Tue Mar 03, 2009 12:43 pm |
|
Joined: Mon Mar 02, 2009 2:22 pm Posts: 1
|
In IEEE 1584, dated 2002, on page 6, fourth paragraph, last sentence – “Equipment below 240 V need not be considered unless it involves at least one 125 kVA or larger low impedance transformer in its immediate power supply.â€
Also on page 25, third paragraph, last sentence within the model and testing discussion – “The arc-flash hazard need only be considered for large 208 V systems: systems fed by transformers smaller than 125 kVA should not be a concern.â€
I am working on Arc flash study for a small electric cooperative. Majority of our transformers are below 125 kVA size. I was wondering if anybody is using this as an option for not considering the arc flash study results for transformer less than 125 kVA.
Any input would be appreciated.
Thanks
|
|
Top |
|
 |
ekalbs4
|
Post subject: Posted: Fri Jul 24, 2009 8:48 am |
|
Joined: Wed Jun 24, 2009 4:45 pm Posts: 41 Location: WA State
|
I'm also wondering the same thing. If you have a bank of three single phase overhead 100 kVA transformers at 208Y/120, is this to be excluded by IEEE 1584 because it is <240V and no single unit is >125 kVA, or is it to be included in analysis, even though <240V, because the bank is 300 kVA, which is greater than the 125 kVA threshold?
|
|
Top |
|
 |
|