i found that IEEE 1583 provides the gap and distance information for 15kV below.May i know how to find the gap between conductors (mm) and distance, x factor for 33kV and 132kV?

Thank you....


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Aug 30, 2009 7:24 pm 
Offline
Sparks Level

Joined: Tue Feb 24, 2009 7:05 am
Posts: 252
Above 15kV, you can't use the IEEE equations based on the stuff they blew up and the associated statistical analysis.
You must use the theoretical IEEE equations which is simpler and doesn't have the X factor and gap.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Aug 31, 2009 6:20 pm 
Offline

Joined: Thu Jul 23, 2009 10:30 am
Posts: 12
Dear Vincent,

Sorry that i didn't get your point. Do you mind to mention the theoretical IEEE equations which are used to calculate the incident energy for the 33kV and 132kV? Thousand thanks.

Yuna


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Aug 31, 2009 6:29 pm 
Offline
Sparks Level

Joined: Tue Feb 24, 2009 7:05 am
Posts: 252
See Equations D.7.4 and D.7.5(b) in Annex D of NFPA 70E-2009.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Aug 31, 2009 7:10 pm 
Offline

Joined: Thu Jul 23, 2009 10:30 am
Posts: 12
Dear Vincent,

i only manage to download the IEEE 1584 from my university. I fail to get the NFPA 70E-2009. can you write up the equaption? where can i manage to get the NFPA 70E? Thanks a lot...


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Sep 01, 2009 2:16 am 
Offline
Sparks Level

Joined: Tue Feb 24, 2009 7:05 am
Posts: 252
There's supposedly a view-only version available from the NFPA (http://www.nfpa.org). Else you can buy it (pdf or paper) at the same location.

I never had access to the full IEEE 1584, only what is quoted in NFPA 70E. So I can't tell you what are the equations number in it.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Sep 14, 2009 10:55 am 
Offline
Sparks Level
User avatar

Joined: Wed Jun 10, 2009 5:00 pm
Posts: 204
Location: Toronto
check Help file for Arc Flash Analytic v5.0 for 15kV+ system equations.

_________________
Michael Furtak, C.E.T.
http://arcadvisor.com


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 7 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883