| Arcing Time for 132kV https://brainfiller.com/arcflashforum/viewtopic.php?f=8&t=661 |
Page 1 of 1 |
| Author: | Yuna [ Thu Sep 17, 2009 12:17 am ] |
| Post subject: | Arcing Time for 132kV |
i intrested to do hand calculation for arc flash hazard for 33kV and 132kV. I face some problem in finding arcing time. May i know is arcing time equal to fault clearing time? How to get the arcing time for 33kV and 132kV switchgear and cables? Is it any standard that i can refer to? Thanks in advance. Yuna |
| Author: | acobb [ Thu Sep 17, 2009 4:01 am ] |
| Post subject: | |
The fault/arc clearing time will be determined by the protective device types and settings. These must be found from calibration/testing reports or by actual field tests for each device. There is no standard for that. Alan |