 Post subject: SHELTER POWER IE ANALYSIS
PostPosted: Wed Jan 29, 2025 3:33 pm 

Joined: Fri Jan 24, 2025 8:31 am
Posts: 3
My company produces shelters for harsh environments. Normally the shelters have a 208/120V input however this project I am working on has a requirement for a 380V/220V. I am looking to hook a transformer to power the shelter for basic tests and verification and would like to ensure the risk of an arc flash is minimal. When I look at the 462 tables and decision diagram it looks like I would have to do an incident energy analysis. I found a few online calculators and have come up with an IE less than 1 cal/cm^2. Would someone be willing to do an informal check based on the attached diagram and run it through ETAP? We do not have a license for it since we would not use it enough. I would like to get something done informally and then take it to get a proper analysis done if there is discrepancy.


Attachments:
shelter pwr sld.jpg
shelter pwr sld.jpg [ 58.11 KiB | Viewed 12687 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: SHELTER POWER IE ANALYSIS
PostPosted: Wed Jan 29, 2025 4:13 pm 
Sparks Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 378
Location: Indiana
Hard to see your image on my phone but it looks like you only have a 9 kva transformer. If so, I expect your available fault current wouldn't be high enough to sustain an arc fault.

_________________
SKM jockey for hire
PE in 16 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: SHELTER POWER IE ANALYSIS
PostPosted: Thu Jan 30, 2025 7:09 am 

Joined: Fri Jan 24, 2025 8:31 am
Posts: 3
Correct, 9KVA


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: SHELTER POWER IE ANALYSIS
PostPosted: Fri Jan 31, 2025 5:24 am 
Sparks Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 378
Location: Indiana
I don't know your available fault current, your proposed cable sizes or lengths, your proposed exact fuses, etc. so I am guaranteeing nothing about the screen captures below. SKM does confirm however that with such low fault currents, and your 12A fuse blowing very quickly, IE is likely extremely low.

Attachment:
SHELTER MODEL 1.jpg
SHELTER MODEL 1.jpg [ 185.43 KiB | Viewed 12678 times ]


Attachment:
SHELTER MODEL 2.jpg
SHELTER MODEL 2.jpg [ 121.3 KiB | Viewed 12678 times ]


Attachment:
SHELTER MODEL 3.jpg
SHELTER MODEL 3.jpg [ 135.37 KiB | Viewed 12678 times ]


Attachment:
SHELTER MODEL 4.jpg
SHELTER MODEL 4.jpg [ 466.68 KiB | Viewed 12678 times ]

_________________
SKM jockey for hire
PE in 16 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: SHELTER POWER IE ANALYSIS
PostPosted: Fri Jan 31, 2025 6:51 am 

Joined: Fri Jan 24, 2025 8:31 am
Posts: 3
Thank you very much bbaumer! I'm going to bring this to the shop manager, and see how they want to proceed!


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883