cbauer wrote:
The breakers need to be "switch duty rated".
Switch Duty Rating (SWD) breakers are for 1-pole 15A and 20A only. The SWD rating is for fluorescent lighting, and UL testing is similar to that of standard light switches.There is a similar rating for High Intensity Discharge lighting, which includes multi-pole breakers up to 50 or 60A.
Other than these additional tests, all breakers are simply endurance tested for electrical and mechanical operations (with and without current), based on 'frame' size and at .80 PF (i.e. 100A< rated for 6,000 @ 100%, and 4,000 @ 0%).