ekstra   ara
 Post subject: CSA Z463
PostPosted: Fri Dec 07, 2012 12:44 pm 
Sparks Level

Joined: Mon Apr 14, 2008 7:10 am
Posts: 142
A new standard Z463 is available for the maintenance of electrical system. Anyone has reviewered the standards and how much it impacts arc flash study from Z462?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Dec 17, 2012 6:48 am 
Sparks Level

Joined: Sun Sep 23, 2007 5:00 pm
Posts: 134
Location: Calgary, Alberta, Canada
It doesn't impact your engineering incident energy analysis study at all. I am on the CSA Z463 Technical Committee. CSA Z463 will emphasize the need for some form of electrical equipment maintenance to be completed in an effort to manage the accuracy of the calculations performed. This would be applicable to protection and coordination as well.

People need to realize that this whole thing is not about "arc flash." Electrical shock is the higher risk of exposure to all workers on a worksite. The probability of an arcing fault and and an arc flash occurring was and is low.

Do you have an Electrical Safety Program in place?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Dec 20, 2012 9:22 am 
Sparks Level

Joined: Mon Apr 14, 2008 7:10 am
Posts: 142
Thanks Terry! We are a consultant company and one of our business is to provide Arc flash hazard analysis for our clients.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883