 Post subject: CSA Z462 - Equation D.7.3(a)
PostPosted: Tue Nov 11, 2014 7:55 am 
Sparks Level

Joined: Mon Apr 14, 2008 7:10 am
Posts: 142
The equation in CSA Z462 is not correct. the number 0.6621gIbf should be 0.662lgIbf. I know that new Z462 is coming and hopefully they will fix it in new version.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: CSA Z462 - Equation D.7.3(a)
PostPosted: Tue Nov 11, 2014 9:52 am 
Sparks Level

Joined: Mon Apr 14, 2008 7:10 am
Posts: 142
I have done the manual calculation for the En in accordance with equation D.7.4 (a), The result of En (incident energy at working distance) is much bigger than the result I got from PTW32. I just want to compare the both and see how much different between software result and manual calculation. Has anyone done this kind of verification before and can share any experience in this group? Same problem for E calculation too.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: CSA Z462 - Equation D.7.3(a)
PostPosted: Mon Nov 17, 2014 7:52 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
Interesting. Expanded a bit, the equations is 0.662 x Log(Ibf) and is right out of the IEEE 1584 standard. Log is "base 10 Logarithm" To my knowledge, all of the software bases their calculation algorithms on these equations and should result in the same answer.

What were the two results?


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883