 Post subject: Conversion error in CSA Z462-08 Annex D?
PostPosted: Wed Mar 04, 2009 7:10 am 
Sparks Level

Joined: Tue Feb 24, 2009 7:05 am
Posts: 252
Hello there,

In equation D.5.2(a) of Annex D of CSA Z462-08, the exponent of D_A is -0.9246. In equation D.5.1(a) of Annex D of NFPA 70E 2009, it's -1.9593. The two following sample calculations give the same Incident Energy given the same input data.

All this seem OK, until you try some other value of D_A with both equations. Then you don't get the same results.
Somebody fuddled with the exponent of D_A so the sample calculation worked out OK, but you can't do that as all other values of D_A won't give you the same results.

I propose the following to replace equation D.5.2(a) of Annex D of CSA Z462-08:
E_MA = 5271 x 25.4^1.9593 x D_A^-1.9593 x t_A x [0.0016F^2 - 0.0076F + 0.8938]
which could be simplified in
E_MA = 2981000 x D_A^-1.9593 x t_A x [0.0016F^2 - 0.0076F + 0.8938]

Also, in CSA Z462-08, the definition of D_A for equation D.5.2(a) says it's in inch, when it should be in mm.

The same conversion mistake has been made in equation D.5.3(a) of CSA Z462-08. I propose the following to replace equation D.5.3(a) of Annex D of CSA Z462-08 (once simplified):
E_MB = 587460 x D_A^-1.4378 x t_A x [0.0093F^2 - 0.3453F + 5.9675]

Any comments on this?
To who should I report this?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Mar 04, 2009 7:34 am 
Sparks Level

Joined: Tue Feb 24, 2009 7:05 am
Posts: 252
A typo this time...

In D.7.3 of Annex D of CSA Z462-08, the definition for K says:
Quote:
K = -0.153 for open-air arcs
K = 0.097 for arcs in a box

In D.7.2 of Annex D of NFPA 70E 2009, the same definitions for K says:
Quote:
K = -0.153 for open-air arcs; -0.097 for arcs-in-a-box


I don't have IEEE 1584 to compare what that standard says.

To who should I report this?
Thanks.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Mar 05, 2009 11:45 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 532
1584 agrees with 70E.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Mar 05, 2009 11:57 am 
Sparks Level

Joined: Tue Feb 24, 2009 7:05 am
Posts: 252
So CSA Z462-08 is in need of a correction.

I'll look into how to do this.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Mar 22, 2009 9:26 am 
Sparks Level

Joined: Sun Sep 23, 2007 5:00 pm
Posts: 114
Location: Calgary, Alberta, Canada
Vincent:

I am on the CSA Z462 Technical Committee, next meeting is in Regina, April 1-2.

We are treating all comments as formal requests for clarification, we need this to happen.

Can you email me your comments so I can follow up formally

Regards;
Terry Becker
http://www.esps.ca
[email protected]


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Mar 23, 2009 5:27 am 
Sparks Level

Joined: Tue Feb 24, 2009 7:05 am
Posts: 252
Sure Terry. I'll do it so we get a better CSA Z462 in the end, one we can trust.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883