Typically, all major equipment, panels, MCCs etc. 46%  46%  [ 21 ]
We often include equipment such as motors, process equipment, J-boxes, etc. 48%  48%  [ 22 ]
Something else 7%  7%  [ 3 ]
Total votes : 46
Author Message
 Post subject: Arc Flash Labels - How Far?
PostPosted: Sun Aug 26, 2012 2:28 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1736
Location: Scottsdale, Arizona
How far do you take the arc flash labeling?
  • Typically all major equipment: Panels, MCCs, Switchboards etc.
  • We often include equipment such as motors, process equipment, J-boxes etc.
  • Something else

There are usually a lot of varied opinions about this one. Let us hear yours.

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Aug 27, 2012 5:56 am 
User avatar

Joined: Mon Aug 20, 2012 10:20 am
Posts: 6
Location: Elgin, Illinois
The intent of NEC 110.16 and NFPA 70E is that any equipment over 50 volts that is likely to be opened while energized for examination, adjustment, servicing, or maintenance must be evaluated for arc flash hazards to warn qualified workers and be labeled with the Arc Flash boundary, Voltage, and at least one of the following: (1) Possible incident energy and working distance; (2) Highest Hazard Risk Category; (3) Minimum Arc Rating of PPE: or (4) Required Level of PPE


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Sep 24, 2012 7:06 pm 
Sparks Level

Joined: Thu Oct 18, 2007 7:10 pm
Posts: 262
Location: NW USA
How many guys work on motor terminal boxes while the motor is running? That is why we generally stop the labels at the MCC. I am aware of one agency that IR scans motor terminals and is interested in labelling the terminal boxes, but that is an exception.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Sep 24, 2012 7:17 pm 
User avatar

Joined: Mon Aug 20, 2012 10:20 am
Posts: 6
Location: Elgin, Illinois
Oftentimes, the Arc Flash incident energy is greater at the motor terminals than at the MCC. The added impedance of the cables lowers the arcing current and slows down the opening time of the breaker or fuse, increasing the possible Arc Flash incident energy at the motor terminals.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883