Hi
I am struggling to understand where the figures in the above sample calculation step 1 are derived. I can see that 610/457.2 ^1.641 = 1.60506
but
12,670/8286^1.641= 2.009.
Can anyone help me understand where these figures are derived
:confused:
thanks
PostPosted: Wed Oct 17, 2012 3:04 am
clive rayner wrote:
Hi
but
:confused:
thanks
The information shown is for adjusting the incident energy from the normalized working distance of 24 inches (610 mm) to your distance of 18 inches (457) mm.
The adjustment is based on the ratio of the two distances raised to the exponent of 1.641 The theoretical exponent was traditionally “2� but IEEE testing shows that this value varies depending on equipment type. 1.641 is for a panel.
The basic concept is the incident energy decreases exponentially with increasing distance. It also increases exponentially as the distance decreases.
As far as the calculations, here is what I have:
(610/457.2)^1.641 = 1.605
Or as IEEE has it in their equations:
(610^1.641) / ( 457.2^1.641)
37215.7 / 23,186.5 = 1.605
The result of 1.605 means that the incident energy will increase by a factor of 1.605 when a person moves from the normalized distance of 24 inches to a working distance of 18 inches.
Hope this helps.
PostPosted: Thu Oct 18, 2012 4:00 am
Hope this helps.
Hi Jim
Good to hear from you again, we met last week at Haydock Park in the U.K.
Thanks for the reply.
thanks