 Post subject: Determination of Incident Energy
PostPosted: Thu Feb 21, 2013 11:27 am 

Joined: Thu Feb 21, 2013 10:56 am
Posts: 4
Hello Folks,

I have a few questions related to DC arc flash calculations. I am in the process of creating a MathCAD template for DC arc flash calculations. I have encountered some confusion with the incident Energy equations, in particular the variable units, for Stokes & Oppenlander and Paukert methods.

The equation for open air:

E_OpenAir = Earc / (4*pi*d^2) = Iarc^2*Rarc*tarc/(4*pi*d^2) = Varc*Iarc*tarc/(4*pi*d^2)

Correct me if I am wrong, but Varc is in Volts, Iarc in amperes, tarc in seconds; d (working distance, typical 18 inches = 45.72 cm) in centimeters. Now, I have conflicting information if where E_OpenAir is in J/cm^2 or cal/cm^2. ETAP
Arc Flash Session 3 at 00:58, which is from the ETAP tutorial, shows that E_OpenAir is in cal/cm^2. However, instinctively, I think that this is wrong and should be in J/cm^2 as V*I*t is in W*s which is Joules.....

Likewise, for the box/enclosure equation:

E_Box = k * Earc / (a^2 + d^2).

I think that "a", which is the reflectivity coefficient, should be in centimeters. Typical should be then 10 cm, 40 cm, 95 cm. Again, E_Box should be in J/cm^2.... Confirm please.

Lastly, the incident energy calculation for maximum power:

E_open = 0.01 * Vsys * Isys * Tarc / D^2;
E_box = 3*0.01 * Vsys * Isys * Tarc / D^2; D is the working distance expressed in cm.
Although Vsys*Isys*Tarc yields W*s = Joules, I reckon that E_open is in cal/cm^2 due to that unexplained "0.01" factor, which somehow converts that equation from Joules to calories??? If there is a source to clear this up, it would be great. Annex D.8.1.1 of NFPA 70E-2012 does suggest it is in cal/cm^2, however some backup rationale on this would really clear this up.

Could someone please give me some insight on this?

Thank you.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Feb 23, 2013 5:23 pm 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2178
Location: North Carolina
These are all empirical equations. Thus units cannot be varied. The corrections are buried in the constant.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883